Had new 220 outlet installed but get fault light

Tue Oct 23, 2018 7:16 pm

I had a 220 outlet installed to charge my 2018 Leaf, but I get a fault light on the EVSE when I plug everything in...what’s up?

GerryAZ
Gold Member
Posts: 1877
Joined: Mon Nov 22, 2010 6:47 pm
Delivery Date: 12 Jun 2011
Location: Phoenix, AZ

Re: Had new 220 outlet installed but get fault light

Tue Oct 23, 2018 7:38 pm

A couple of possibilities:
1. Wiring problem with new receptacle circuit (such as improper ground or lose connections).
2. Low voltage if you are using the dual-voltage Nissan EVSE that came with the car. It is documented in other threads on this forum that the Nissan dual voltage EVSE will not work on 208-volt circuits which are common in industrial/commercial facilities.

In either case, have the receptacle wiring and actual circuit voltage checked/repaired by a qualified electrician. The voltage should be about 240 volts if you intend to use the Nissan dual-voltage EVSE.
Gerry
Silver LEAF 2011 SL rear ended (totaled) by in-attentive driver 1/4/2015 at 50,422 miles
Silver LEAF 2015 SL purchased 2/7/2015

smkettner
Posts: 7221
Joined: Mon Aug 09, 2010 10:13 pm
Delivery Date: 26 Feb 2014
Location: Orange County, CA

Re: Had new 220 outlet installed but get fault light

Tue Oct 23, 2018 7:48 pm

Yes measure the actual voltage between the hots, s/b very close to 240.
Then measure voltage of each hot to ground, s/b very close to 120 each.

Post the results.
1 bar lost at 21,451 miles, 16 months.
2 bar lost at 35,339 miles, 25 months.
LEAF traded at 45,400 miles for a RAV4-EV
I-Pace on order for end of 2018 delivery

Bouldergramp
Posts: 24
Joined: Mon Oct 15, 2018 10:36 am
Delivery Date: 15 Oct 2018
Leaf Number: 317621
Location: COLORADO

Re: Had new 220 outlet installed but get fault light

Tue Oct 23, 2018 7:49 pm

You can start by looking at page 92 of the 578 page manual although I don't think it is very clear. My outlet has a little over 240V between the two opposing vertical slots in the outlet and a little over 120V between each of those slots and ground, the bottom vertical slot.

I wonder how many people have multimeters these days? Mine must be 40 years old.

powersurge
Posts: 1133
Joined: Wed Oct 21, 2015 10:24 am
Delivery Date: 06 Dec 2014
Location: Long Island, NY

Re: Had new 220 outlet installed but get fault light

Wed Oct 24, 2018 9:17 am

Everybody should have multimeters nowadays, they are so cheap.... They even give them away at Harbor Freight stores...

Rigatony
Posts: 8
Joined: Tue Oct 23, 2018 6:24 pm
Delivery Date: 24 Oct 2018
Leaf Number: 304248

Re: Had new 220 outlet installed but get fault light

Wed Oct 24, 2018 1:36 pm

The Electrical contractor says it could be a bad ground from the main ground wire within the foundation. When I plug the EVSE in the outlet the power light indicator is on, when I plug it into the car the normal activity starts and only after about 10 second the EVSE goes to fault.

User avatar
davewill
Posts: 4990
Joined: Thu Mar 17, 2011 6:04 pm
Location: San Diego, CA, US

Re: Had new 220 outlet installed but get fault light

Wed Oct 24, 2018 2:38 pm

Rigatony wrote:The Electrical contractor says it could be a bad ground from the main ground wire within the foundation. When I plug the EVSE in the outlet the power light indicator is on, when I plug it into the car the normal activity starts and only after about 10 second the EVSE goes to fault.

So it could, but I'd be more suspicious of the new work than the old work.
2014 Rav4 EV, Blizzard Pearl White
2011 LEAF SL w/QC, Blue Ocean, returned at end of lease

LeftieBiker
Moderator
Posts: 9875
Joined: Wed May 22, 2013 3:17 am
Delivery Date: 30 Apr 2018
Location: Upstate New York, US

Re: Had new 220 outlet installed but get fault light

Wed Oct 24, 2018 3:14 pm

You can get a ground tester cheap. You can also just use an electrician's test light and test between Hot(s) and Ground. If the light is strong and unwavering the ground is likely good.
Scarlet Ember 2018 Leaf SL W/ Pro Pilot
2009 Vectrix VX-1 W/18 Leaf modules, & 3 EZIP E-bicycles.
PLEASE don't PM me with Leaf questions. Just post in the topic that seems most appropriate.

smkettner
Posts: 7221
Joined: Mon Aug 09, 2010 10:13 pm
Delivery Date: 26 Feb 2014
Location: Orange County, CA

Re: Had new 220 outlet installed but get fault light

Wed Oct 24, 2018 7:39 pm

Rigatony wrote:The Electrical contractor says it could be a bad ground from the main ground wire within the foundation. When I plug the EVSE in the outlet the power light indicator is on, when I plug it into the car the normal activity starts and only after about 10 second the EVSE goes to fault.

EVSE has no idea where and how the ground is connected. EVSE may check voltage to the hots and that is about it. If there is a neutral it may check neutral/ground potential and continuity but most L2 EVSE has no neutral.

Have the handyman check the voltage potentials and post right here.
1 bar lost at 21,451 miles, 16 months.
2 bar lost at 35,339 miles, 25 months.
LEAF traded at 45,400 miles for a RAV4-EV
I-Pace on order for end of 2018 delivery

User avatar
davewill
Posts: 4990
Joined: Thu Mar 17, 2011 6:04 pm
Location: San Diego, CA, US

Re: Had new 220 outlet installed but get fault light

Thu Oct 25, 2018 9:16 am

smkettner wrote:
Rigatony wrote:The Electrical contractor says it could be a bad ground from the main ground wire within the foundation. When I plug the EVSE in the outlet the power light indicator is on, when I plug it into the car the normal activity starts and only after about 10 second the EVSE goes to fault.

EVSE has no idea where and how the ground is connected. EVSE may check voltage to the hots and that is about it. If there is a neutral it may check neutral/ground potential and continuity but most L2 EVSE has no neutral.

Have the handyman check the voltage potentials and post right here.

Most EVSEs leak a little current to ground to test during initialization. A poor or disconnected ground can be detected this way. I find it much more likely that the electrician goofed his install rather than the house ground being bad.