goldbrick
Posts: 539
Joined: Tue Aug 01, 2017 3:33 pm
Delivery Date: 01 Aug 2017
Leaf Number: 311806
Location: Boulder, CO

Re: Specs for 240v outlet/breaker

Wed Jun 26, 2019 4:10 pm

You could run 8 THHN in conduit to a junction box somewhere convenient and then finish the run with 6 NM-B. Not sure if that would help as every case is different but it's something to consider.

RustyShackleford
Posts: 95
Joined: Mon Jun 24, 2019 4:59 pm
Delivery Date: 0- 0-2018
Location: central NC

Re: Specs for 240v outlet/breaker

Wed Jun 26, 2019 4:24 pm

goldbrick wrote:You could run 8 THHN in conduit to a junction box somewhere convenient and then finish the run with 6 NM-B. Not sure if that would help ...
Thanks, but won't help; inside the main panel is where I'm really loathe to have to deal with 6awg conductors (even outside the sheath). I think I can make conduit work though, transitioning to the semi-flexible stuff between the floor and the box.
2018 Nissan Leaf SV
2006 Subaru Outback 2.5i Ltd