Re: Safe to charge via dryer outlet?

Tue Sep 02, 2014 7:36 pm

LeftieBiker wrote:Yes, that's why I suggested an either/or switch.
30 Amp manual xfer switch (generator panel) feeding 2 permanent 30A outlets 14-30R & 6-30R, but money would be better spent on a chunk of 8/3 loomex or teck cable c/w 40A breaker for the EVSE. The breaker will run cooler and from what I've seen in the field most L2 EVSE's manufacturer specs require this. Canadian electric code would would require 2 dedicated circuits. I can't see it any different in the States.
Pearl White Sl
mfd date 09/16

QueenBee
Posts: 1564
Joined: Sun Aug 08, 2010 5:14 pm
Delivery Date: 20 Jun 2011
Leaf Number: 2062
Location: Portland

Re: Safe to charge via dryer outlet?

Tue Sep 02, 2014 11:35 pm

TonyWilliams wrote:
Graffi wrote:Leave both the dryer and the EVSE plugged in all the time, but NEVER use the dryer when the EV is charging.
That is neither code, nor safe.

You are literally betting a possible fire that the circuit breaker will save the day.
Same could be said about having multiple receptacles on a 120 volt circuit. Circuit breakers save the day thousands and thousands of times a day.

NEC allows multiple 240 volt receptacles on one circuit so I'm wondering what would preclude someone from doing this (besides the obvious thing that it is a bit silly and not nearly as safe as a dedicated circuit.)

User avatar
Stanton
Posts: 2270
Joined: Thu Feb 03, 2011 10:56 am
Delivery Date: 01 Sep 2011
Leaf Number: 7458
Location: Plano, TX
Contact: Website Twitter

Re: Safe to charge via dryer outlet?

Wed Sep 03, 2014 7:10 am

Besides literally "playing with fire", I don't understand why someone would risk a $30k+ automobile on poor/risky EVSE implementations. For the record, I have used an EVSEUpgrade unit on a dedicated dryer socket in my garage since I bought my Leaf with no issues (I rarely plug/un-plug the unit).
2011 Blue Ocean SV w/floor mats & window tint
Lithium Pros 12v LiFePO4 battery w/Antigravity Battery Tracker
FIAMM 74100 horns
Wet Okole seat covers
Tor's low-power heater mod
2013 sun visor
Battery Pack replaced (Rev E) @51 months and 41k miles

User avatar
Nubo
Posts: 5838
Joined: Fri May 28, 2010 11:01 am
Delivery Date: 31 Oct 2014
Location: Vallejo, CA

Re: Safe to charge via dryer outlet?

Wed Sep 03, 2014 7:54 am

QueenBee wrote:Same could be said about having multiple receptacles on a 120 volt circuit. Circuit breakers save the day thousands and thousands of times a day.
Two heavy-draw devices on a 240V circuit is essentially a planned, deliberate and extreme overload at high power levels. Breakers save the day, yes that's their job. But still, don't take foolish chances. Breakers can and do fail. 240V devices by their nature are both high-voltage and high-amperage. While overloads of any type are to be avoided, they're generally more severe in the case of 240V circuits. And there's a difference between an incidental overload, and designing an overload.
I noticed you're still working with polymers.

QueenBee
Posts: 1564
Joined: Sun Aug 08, 2010 5:14 pm
Delivery Date: 20 Jun 2011
Leaf Number: 2062
Location: Portland

Re: Safe to charge via dryer outlet?

Sun Sep 07, 2014 8:27 pm

Nubo wrote:
QueenBee wrote:Same could be said about having multiple receptacles on a 120 volt circuit. Circuit breakers save the day thousands and thousands of times a day.
Two heavy-draw devices on a 240V circuit is essentially a planned, deliberate and extreme overload at high power levels. Breakers save the day, yes that's their job. But still, don't take foolish chances. Breakers can and do fail. 240V devices by their nature are both high-voltage and high-amperage. While overloads of any type are to be avoided, they're generally more severe in the case of 240V circuits. And there's a difference between an incidental overload, and designing an overload.
Anyway my point was just regardless of your opinion the NEC does allow multiple receptacles on a 240 volt circuit.

There are lots of situations were 240 volt with high amperage is designed that you aren't going to turn everything on at once and if you do that a circuit breaker/fuse is going to protect the wires. For example maxing out every circuit in your house will overload your service. If you and your neighbors all use too much power you'll overload the likely 25kva transformers that are often shared among many homes.

But like I said it's a bit silly and not nearly as safe as a dedicated circuit.

User avatar
garygid
Gold Member
Posts: 12469
Joined: Wed Apr 21, 2010 8:10 am
Delivery Date: 29 Mar 2011
Leaf Number: 000855
Location: Laguna Hills, Orange Co, CA

Re: Safe to charge via dryer outlet?

Sun Sep 07, 2014 10:13 pm

Technically, the 3-prong dryer socket is ungrounded, wired as 2 hot lines and the Neutral, right?

Then, the dryer is allowed to use the 10-30 Neutral slightly incorrectly as the chassis Ground, right?
See SOC/GID-Meter and CAN-Do Info
2010 Prius
2011 LEAF, 2014 Tesla S85
2018 & 2019 Tesla Model 3
PU: SDG&E
Solar PV: 33 x 225W -> 7 kW max AC
Craigslist: Xm5000Li Electric Motorcycle

QueenBee
Posts: 1564
Joined: Sun Aug 08, 2010 5:14 pm
Delivery Date: 20 Jun 2011
Leaf Number: 2062
Location: Portland

Re: Safe to charge via dryer outlet?

Sun Sep 07, 2014 10:56 pm

garygid wrote:Technically, the 3-prong dryer socket is ungrounded, wired as 2 hot lines and the Neutral, right?

Then, the dryer is allowed to use the 10-30 Neutral slightly incorrectly as the chassis Ground, right?
I guess that would be sora true since you'd connect this to the nuetral bus bar if they were seperated in the panel but I guess you could also say that it's technically the EGC and nuetral wire.

CGKyle
Posts: 2
Joined: Fri Jan 30, 2015 6:17 am
Delivery Date: 30 Apr 2015
Location: Louisville KY

Re: Safe to charge via dryer outlet?

Wed Feb 25, 2015 7:32 am

I've found this thread incredibly helpful. In my case I plan to extend my existing #10 wire another 10 feet from my dryer circuit through the wall into the garage. I'm having an electrician buddy do the work but I've already purchased an industrial grade 30 amp double pole double pole switch as suggested in this thread. It looks like a standard switch so the spouse can use it without intimidation. Heavier wire though would require a larger type of switch. Hopefully, like me, others can use this to kickstart their electrician into keeping to code, and keeping the install bills at a minimum. Then with my EVSE Upgrade I have the easiest possible plan for level 2 charging.

QueenBee
Posts: 1564
Joined: Sun Aug 08, 2010 5:14 pm
Delivery Date: 20 Jun 2011
Leaf Number: 2062
Location: Portland

Re: Safe to charge via dryer outlet?

Wed Feb 25, 2015 10:21 am

CGKyle wrote:Heavier wire though would require a larger type of switch.
If the switch is not rated to accept a larger gauge wire one thing electricians will do is add a pig tail with the the largest gauge it does accept and then use the proper size wire nut.

Rauv
Posts: 127
Joined: Mon Mar 05, 2012 10:04 am
Delivery Date: 31 May 2012
Leaf Number: 19000
Location: Twin Cites, MN

Re: Safe to charge via dryer outlet?

Wed Feb 25, 2015 11:37 am

You are not allowed to use the dryer outlet for an EVSE. This is new to the 2014 NEC. See Art 210.17:

"An outlet(s) installed for the purpose of charging electric vehicles shall be supplied by a separate branch circuit. This circuit shall have no other outlets."

Check to see what Code cycle your town uses.
2013 Cayenne SL [70 months][45000 mi][11 bar]
GE Wattstation 7.2kw EVSE + EVSE Upgrade (16A)
5.67 kw PV System. 3-ton GSHP