HELP: OEM EVSE tripping outlet's GFCI

Sat Apr 30, 2011 9:32 pm

So I picked up my LEAF today :D, drove around a whole bunch, came home, plugged the car into an 120V outlet (with GFCI) in the garage to charge. The EVSE's charge light would go on, but within less than a minute, the GFCI would trip :( . This happens consistently. Should that be happening?

More info:
* My house was built around 1989.
* I have a compressor (Campbell-Hausfeld VT6316) plugged into the wall plate's other outlet. The compressor's label reads: "wired for 120V / 15A / 60 Hz / 1PH". I have used the compressor many many years without it tripping the GFCI. For example, when the compressor's tank is empty, to fill it up to use pressure (usually 100 psi), the compressor would have to run at least five minutes. It seems to me that if the outlet can support 15 amps for that long, why would the OEM EVSE trip the GFCI after less than a minute? (I even tried unplugging the compressor and plugging the OEM EVSE into its outlet: same result.)
* I am using a 50-feet 12-gauge grounded extension cord between the outlet and the OEM EVSE. Can the cord's length be causing this problem?

What is the likelihood that there is something wrong with my OEM EVSE? With my outlet? Thanks for any clues.
Anna Nguyen

Glenn
Posts: 281
Joined: Sat Sep 04, 2010 6:32 pm
Delivery Date: 02 Jul 2011
Location: Oakland, CA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sat Apr 30, 2011 10:03 pm

aqn wrote:* I am using a 50-feet 12-gauge grounded extension cord between the outlet and the OEM EVSE. Can the cord's length be causing this problem?
I never stayed at a Holiday Inn Express, but I'm willing to bet a bundle that you self-diagnosed your problem...

Glenn

User avatar
garygid
Gold Member
Posts: 12469
Joined: Wed Apr 21, 2010 8:10 am
Delivery Date: 29 Mar 2011
Leaf Number: 000855
Location: Laguna Hills, Orange Co, CA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sat Apr 30, 2011 10:42 pm

Often/sometimes/occasionally the GFI in standard sockets is too sensitive for use with the EVSE. The EVSE includes a less-sensitive GFI.

Try a non-GFI outlet.
See SOC/GID-Meter and CAN-Do Info
2010 Prius
2011 LEAF, 2014 Tesla S85
2018 & 2019 Tesla Model 3
PU: SDG&E
Solar PV: 33 x 225W -> 7 kW max AC
Craigslist: Xm5000Li Electric Motorcycle

User avatar
GeekEV
Posts: 1825
Joined: Tue Jan 18, 2011 4:11 pm
Delivery Date: 15 Feb 2011
Leaf Number: 0308
Location: NorCal, USA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sat Apr 30, 2011 11:30 pm

I used mine on a GFCI outlet a few times and it was fine, though it did pop prematurely once... You could try replacing the GFCI outlet with a newer model. Yours may be too sensitive.

2014 Chevy Spark EV 2LT
2013 Tesla Model S 60kWh[/url]
AV L2 EVSE + kWh meter
9.4kW Solar Array + enphase energy

User avatar
gbarry42
Posts: 888
Joined: Mon Jan 10, 2011 5:48 pm
Delivery Date: 06 May 2011
Location: Moonlight Beach

Re: HELP: OEM EVSE tripping outlet's GFCI

Sat Apr 30, 2011 11:43 pm

aqn wrote: It seems to me that if the outlet can support 15 amps for that long, why would the OEM EVSE trip the GFCI after less than a minute?
A ground fault involves detecting the presence of a small leakage current. The amount of current the outlet can supply has nothing to do with this. Try another extension cord if possible (only because that's the only easy thing you can try). The EVSE could be faulty, as could the car. But my vote goes with the others--it's usually the outlet itself being too sensitive.
And there goes the first capacity bar! At 24,000 mi on 9/9/2013.
Second bar at 30,500 mi on 2/7/2015.

User avatar
davewill
Posts: 5083
Joined: Thu Mar 17, 2011 6:04 pm
Location: San Diego, CA, US

Re: HELP: OEM EVSE tripping outlet's GFCI

Sat Apr 30, 2011 11:48 pm

If at all possible try to eliminate the extension cord, at least for a test. Then at least you'll know whether it's the EVSE or not.
2014 Rav4 EV, Blizzard Pearl White
2011 LEAF SL w/QC, Blue Ocean, returned at end of lease

User avatar
linkim
Posts: 495
Joined: Thu Dec 16, 2010 5:06 pm
Location: Silicon Valley

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 6:46 am

garygid wrote: Try a non-GFI outlet.
I tried a non-GFI outlet (3-prong outlet) in my garage and the EVSE didn't work. However, when the Blink was installed, the electrician said there was no ground even though it appeared to be a grounded circuit. It did work on the GFCI circuit but I had to use an extension cord from the kitchen to the garage.
LEAF SL + QC
Reserved: 4/20/10
Received: April 19, 1 year after reservation

User avatar
garygid
Gold Member
Posts: 12469
Joined: Wed Apr 21, 2010 8:10 am
Delivery Date: 29 Mar 2011
Leaf Number: 000855
Location: Laguna Hills, Orange Co, CA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 7:23 am

The L1 EVSE requires a Ground, or it will refuse to work.

Get your sockets properly Grounded.

If the only grounded socket that is available (even with a heavy-duty extension cord) is the GFI socket, consider having that socket replaced with a properly-grounded non-GFI socket.
See SOC/GID-Meter and CAN-Do Info
2010 Prius
2011 LEAF, 2014 Tesla S85
2018 & 2019 Tesla Model 3
PU: SDG&E
Solar PV: 33 x 225W -> 7 kW max AC
Craigslist: Xm5000Li Electric Motorcycle

User avatar
linkim
Posts: 495
Joined: Thu Dec 16, 2010 5:06 pm
Location: Silicon Valley

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 8:45 am

garygid wrote:If the only grounded socket that is available (even with a heavy-duty extension cord) is the GFI socket, consider having that socket replaced with a properly-grounded non-GFI socket.
Sorry, I don't understand what you are saying. The current GFI outlet I used for L1 charging (now have Blink installed) is in the kitchen, which is required by code. Why would you suggest it be replaced by grounded non-GFI? I agree the the outlet in the garage needs to be upgraded to a grounded GFI circuit for L1 charging of my LEAF.

In any case, thanks for your many suggestions/observations to the forum which have helped me to better understand the LEAF.
LEAF SL + QC
Reserved: 4/20/10
Received: April 19, 1 year after reservation

User avatar
aqn
Gold Member
Posts: 820
Joined: Fri Oct 01, 2010 12:59 pm
Delivery Date: 30 Apr 2011
Leaf Number: 1333
Location: Austin, TX

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 8:54 am

Thanks for all the clues so far.

I tried plugging directly into the GFCI outlet: same result. (I verified that the outlets are on a 20-amp breaker.)
I tried plugging directly into another GFCI outlet (outside outlets, on a different 20-amp braker): same result.
I tried plugging it into the washer's outlet (20-amp, non-GFCI; or rather, there is no GFCI test/reset button on it), just inside the garage, via the same 50-feet 12-gauge extension cord: it's charging fine!

In any case, since I'm sending off the OEM EVSE to evseupgrade.com to get it upgraded, and will have an electrician come & install a 240V outlet in my garage, this is not a pressing/do-or-die problem.