Re: 30A Circuit Breaker tripped on Nissan Leaf

Wed Sep 05, 2012 1:35 pm

If the house is wired to share neutrals then modern loads that create harmonics can overload the neutral and cause fires. Have a well-qualified electrician look at your situation.
There is very good reason NEC does not allow shared neutrals anymore.

As for the 30A breaker tripping on overload at 25A, it should not happen on a normal breaker, ... but it could on an old breaker.
2011 SLe 06/17/11 Over 89000 miles 61%SOH 13.8kWh
2018 Honda Clarity PHEV
2014 Model S P85 77888 miles 256mile range
5.7kW DC Solar System

MikeD
Posts: 670
Joined: Thu Jun 24, 2010 6:14 am
Delivery Date: 12 May 2011
Leaf Number: 592

Re: 30A Circuit Breaker tripped on Nissan Leaf

Wed Sep 05, 2012 7:17 pm

camasleaf: I personally would agree that "shared neutrals" should be avoided for several very good safety reasons that I won't go into. However, as I read the 2008 NEC (Article 210.4), shared neutrals are allowed. Was there a change in the 2011 NEC?

cwerdna
Posts: 9732
Joined: Fri Jun 03, 2011 4:31 pm
Delivery Date: 28 Jul 2013
Location: SF Bay Area, CA

Re: 30A Circuit Breaker tripped on Nissan Leaf

Wed Sep 05, 2012 7:31 pm

FairwoodRed wrote:You don’t happen to live in the Seattle area do you?
Yet another reason why the location field should be mandatory.

'19 Bolt Premier
'13 Leaf SV w/premium package (owned)
'13 Leaf SV w/QC + LED & premium packages (lease over, car returned)

Please don't PM me with Leaf questions. Just post in the topic that seems most appropriate.

FairwoodRed
Posts: 459
Joined: Wed May 18, 2011 10:25 am
Location: Fairwood, WA

Re: 30A Circuit Breaker tripped on Nissan Leaf

Thu Sep 06, 2012 9:08 am

cwerdna wrote:
FairwoodRed wrote:You don’t happen to live in the Seattle area do you?
Yet another reason why the location field should be mandatory.
I don't mind asking the question when I want to know. I much prefer each person being able to chose how much information to share, rather than being forced to share regardless of personal want or need. I vote for personal choice!

camasleaf
Posts: 646
Joined: Sun Sep 26, 2010 5:20 am
Delivery Date: 17 Jun 2011
Location: Camas, WA

Re: 30A Circuit Breaker tripped on Nissan Leaf

Thu Sep 06, 2012 1:05 pm

MikeD wrote:camasleaf: I personally would agree that "shared neutrals" should be avoided for several very good safety reasons that I won't go into. However, as I read the 2008 NEC (Article 210.4), shared neutrals are allowed. Was there a change in the 2011 NEC?
I was missinformed it is still alowed in 2011 NEC.

I had a NEC class early this year, and I clearly remember the instructor saying that it was not allowed anymore.
2011 SLe 06/17/11 Over 89000 miles 61%SOH 13.8kWh
2018 Honda Clarity PHEV
2014 Model S P85 77888 miles 256mile range
5.7kW DC Solar System

User avatar
garygid
Gold Member
Posts: 12464
Joined: Wed Apr 21, 2010 8:10 am
Delivery Date: 29 Mar 2011
Leaf Number: 000855
Location: Laguna Hills, Orange Co, CA

Re: 30A Circuit Breaker tripped on Nissan Leaf

Thu Sep 06, 2012 10:20 pm

Or, the breaker is bad, and needs to be replaced.
See SOC/GID-Meter and CAN-Do Info
2010 Prius, now for sale
2011 LEAF, sold in 2015
2018 Tesla Model 3
2014 Tesla S, Model 3 in 2019
PU: SDG&E
Solar PV: 33 x 225W -> 7 kW max AC
To Sell: X-treme 5000Li EV motorcycle

User avatar
planet4ever
Posts: 4674
Joined: Sat Apr 03, 2010 9:53 pm
Delivery Date: 02 May 2011
Leaf Number: 1537
Location: Morgan Hill, CA, south of San Jose

Re: 30A Circuit Breaker tripped on Nissan Leaf

Fri Sep 07, 2012 12:43 am

Even if a breaker is bad, replacing it is not the answer. A 240v circuit should never have 120v taps for garage door openers, solar water heater controllers, sensor lights, and wall plugs. yorkhung needs a 240v circuit which is only used to charge the LEAF.

Ray
End of April 2013: Traded my 2011 SL for a 2013 S with charge pkg.

pchilds
Posts: 418
Joined: Sun Jun 17, 2012 12:14 am
Delivery Date: 31 Jul 2011
Leaf Number: 006141
Location: SoCal

Re: 30A Circuit Breaker tripped on Nissan Leaf

Fri Sep 07, 2012 3:05 am

This garage looks like the one in a house I owned. If the wiring has cloth insulation, you need to get the house rewired, before it burns down. I would guess there have been a lot changes to the wiring in the 50+ years this house has been in use. My guess would be that a sub panel being run off the dryer breaker. My house had one circuit feed from two breakers in two different panels. Old houses are so much fun.
2011 LEAF, gone,
2012 RAV4 EV,
2015 Model S 85D,
Solar PV 5.25 kW system.

User avatar
Nubo
Posts: 5395
Joined: Fri May 28, 2010 11:01 am
Delivery Date: 31 Oct 2014
Location: Vallejo, CA

Re: 30A Circuit Breaker tripped on Nissan Leaf

Fri Sep 07, 2012 11:12 am

I don't know what to make of this thread. On the one hand the OP reports they studied Electrical Engineering. On the other hand the circuit is popping from a 16A load and they talk about swapping the 30A breaker with a 70A. And then that picture! :o.

I don't fancy myself as an electrician by any means and I had a lot of questions here when trying to plan my own EVSE installation. But this really is out there.

Either the OP was having a little fun with us, or I'm worried since they haven't been back for awhile!!
I noticed you're still working with polymers.

gfederas
Posts: 13
Joined: Fri Dec 23, 2011 2:24 pm
Delivery Date: 23 Dec 2011
Leaf Number: 5536

Re: 30A Circuit Breaker tripped on Nissan Leaf

Fri Sep 07, 2012 12:12 pm

I am not an electrician, but when my home was remodeled in 2000, it required a main panel upgrade. I understand that under current code each major appliance requires it's own dedicated breaker. i.e., AC, refrigerator, range/oven, microwave, electric water heater, washer, dryer, etc. There is also a limit to how may plugs can be wired onto a single breaker. It makes sense that 120V circuits have breakers separate from the 240V circuits. A qualified electrician would be familiar with all current codes and can remove any immediate fire hazards, and re-wire the home to current safety standards. Of course, you should get multiple bids from several electricians to perhaps save some money, but every electrician that sees your wiring would come to the same conclusion - it's a fire waiting to happen. I wouldn't sleep at night knowing what you've shared about your electrical wiring. We wouldn't want the next newspaper headline telling the story of how another EV household burned down.