Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 8:59 am

If the socket (like in the kitchen, batheoom, etc.) requires a GFI, do not change it, just do not try to use it for EVSE charging.

Since many GFIs are too sensitive to work reliably with an EVSE, try to use a NON-GFI socket with the EVSE (of course also properly Grounded), a 3-prong (5-15 or 5-20) socket.

In short, do NOT use a GFI socket.

It is OK to try a GFI socket, and OK to use it IF it works with your EVSE and car, but just realize that it MIGHT not work reliably (as you experienced).
See SOC/GID-Meter and CAN-Do Info
2010 Prius
2011 LEAF, 2014 Tesla S85
2018 & 2019 Tesla Model 3
PU: SDG&E
Solar PV: 33 x 225W -> 7 kW max AC
Craigslist: Xm5000Li Electric Motorcycle

Bassman
Posts: 277
Joined: Mon Dec 06, 2010 10:30 am
Location: Angels Camp, CA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 9:03 am

It sounds like your GFCI is too sensitive. A non-GFCI outlet is recommended for most EVSE and when you get the modified L1, you'll most likely need a non GFCI 240 volt outlet also. ;) Phil, Chime in anytime.
Glenn
Ocean Blue SL w/QC,
Delivered 4/29/2011- VIN# 756
34,800 miles so far (2/20/2013) Still 12 bars @ 100% charge, but range has reduced by about 10 to 12 %
2012 Pearl White (Blizzard) Rav4 EV

wwhitney
Posts: 762
Joined: Sat Jul 17, 2010 10:10 am
Delivery Date: 01 Apr 2011
Location: Berkeley, CA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 9:34 am

garygid wrote: Since many GFIs are too sensitive to work reliably with an EVSE, try to use a NON-GFI socket with the EVSE (of course also properly Grounded), a 3-prong (5-15 or 5-20) socket.
While I have heard this before and it is possible, I am dubious because I can't really think of a good reason the EVSE should be leaking current to ground.

To the OP: to eliminate the extension cord as the problem, try running your compressor on the extension cord to see if it pops the GFCI. Most likely, if the GFCI is from 1989, it is subject to false trips due to electrical noise from certain loads. A modern GFCI would hopefully be more robust. Or else the extension cord or the OEM EVSE is in fact faulty.

Cheers, Wayne

DarkStar
Posts: 2066
Joined: Sat Jul 17, 2010 10:06 am
Delivery Date: 25 Mar 2011
Leaf Number: 568
Location: Hillsboro, Oregon, USA
Contact: Website

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 9:36 am

I've been testing my modified EVSE on a variety of GFCI outlets and have never experienced a trip. At most locations I'm using 25 feet of extension cord. Go buy an outlet tester (http://amzn.com/B002LZTKIU) and make sure they're connected up properly.
Mikiko (2011 Nissan LEAF ETEC) Status:
Reserved: 04/20/10 | Ordered: 10/01/10 | EV Project Blink Installed: 03/22/11 | Delivered: 03/25/11 | VIN: 568

Oregon Electric Vehicle Association | Electric Auto Association

User avatar
garygid
Gold Member
Posts: 12466
Joined: Wed Apr 21, 2010 8:10 am
Delivery Date: 29 Mar 2011
Leaf Number: 000855
Location: Laguna Hills, Orange Co, CA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 10:13 am

It is not the EVSE itself that causes the GFI trips, it is the car's charger that can use the power a bit erratically (filling/discharging capacitors, I expect).
See SOC/GID-Meter and CAN-Do Info
2010 Prius
2011 LEAF, 2014 Tesla S85
2018 & 2019 Tesla Model 3
PU: SDG&E
Solar PV: 33 x 225W -> 7 kW max AC
Craigslist: Xm5000Li Electric Motorcycle

DaveinOlyWA
Posts: 14462
Joined: Sat Apr 24, 2010 7:43 pm
Delivery Date: 16 Nov 2019
Leaf Number: 319862
Location: Olympia, WA
Contact: Website

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 11:08 am

The trip circuit is spring loaded and wears out causing circuit trips at less than rated voltages. I would try replacing outlet first. They only cost like $10
2011 SL; 44,598 mi, 87% SOH. 2013 S; 44,840 mi, 91% SOH. 2016 S30; 29,413 mi, 99% SOH. 2018 S; 25,185 mi, SOH 92.23%. 2019 S Plus; 3500.3 mi, 96.95% SOH
My Blog; http://daveinolywa.blogspot.com" onclick="window.open(this.href);return false;

User avatar
gbarry42
Posts: 888
Joined: Mon Jan 10, 2011 5:48 pm
Delivery Date: 06 May 2011
Location: Moonlight Beach

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 11:54 am

Better yet, when the EVSE comes back, you'll know for sure that it has no issues. Might be a good idea to include a note that says to check it before they convert it.
And there goes the first capacity bar! At 24,000 mi on 9/9/2013.
Second bar at 30,500 mi on 2/7/2015.

User avatar
aqn
Gold Member
Posts: 819
Joined: Fri Oct 01, 2010 12:59 pm
Delivery Date: 30 Apr 2011
Leaf Number: 1333
Location: Austin, TX

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 8:13 pm

garygid wrote:The L1 EVSE requires a Ground, or it will refuse to work.

Get your sockets properly Grounded.

If the only grounded socket that is available (even with a heavy-duty extension cord) is the GFI socket, consider having that socket replaced with a properly-grounded non-GFI socket.
FWIW, I turned off the outlet' breaker and opened it up: it is grounded. Or rather, there is a bare copper wire screwed into the outlet's ground screw; I did not verify where the other end of the wire goes, or checked for continuity between it and, say, the outlet's box.

I think I will get an outlet tester per DarkStar and test the outlet's sockets to see what's up, just out of curiosity.
Anna Nguyen

DarkStar
Posts: 2066
Joined: Sat Jul 17, 2010 10:06 am
Delivery Date: 25 Mar 2011
Leaf Number: 568
Location: Hillsboro, Oregon, USA
Contact: Website

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 9:07 pm

aqn wrote:I think I will get an outlet tester per DarkStar and test the outlet's sockets to see what's up, just out of curiosity.
I have one in my adapter bag with an extension cord that is 50 feet of 10-3 and a voltmeter. Never leave home without it! :D
Mikiko (2011 Nissan LEAF ETEC) Status:
Reserved: 04/20/10 | Ordered: 10/01/10 | EV Project Blink Installed: 03/22/11 | Delivered: 03/25/11 | VIN: 568

Oregon Electric Vehicle Association | Electric Auto Association

User avatar
mgoleta
Posts: 200
Joined: Tue Oct 19, 2010 12:55 am
Delivery Date: 21 Apr 2011
Location: Goleta,CA

Re: HELP: OEM EVSE tripping outlet's GFCI

Sun May 01, 2011 9:32 pm

I have only had my car a week and half. I am only using L1 charging. I plug into a standard GFCI at both home at and at work without an extension cord and have never had a single circuit trip (out of about 15 charge cycles, charge durations from 1hr to 10 hrs). I just got my Leviton lighted GFCI outlet and will be installing them at both work and at home ( I like being able to see the outlet in the dark.) If you a relatively recent GFCI outlet or breaker (and not shared with other devices, ie a dedicated outlet and breaker) I would not expect that there would be an issue if your wiring is good. If you still have the problem without the use of an extension cord it may be worthwhile having your wiring looked at by a professional. If the problem goes away without the extension cord and you really need one, get a different cord. It is not worthwhile skimping on he extension cord.
Glacial Pearl 2011 LEAF SL, QC delivered 4/21/2011, sold 7/22/2018
Chevy Bolt Premiere, 6/4/2018
White 2018 LEAF S, QC, Winter package, 6/14/2018