rmay635703 wrote:Just a note most every leaf will charge at least 16amps even on 110vac with a proper EVSE AND outlet.

20amp 120vac circuits are quite common and even the classic 30/50 amp. 110vac RV plugs aren’t unheard of

If he doesn’t care about the 1900 watt charge rate it is possible he could get a 20 amp 110vac outlet and evse.

It’s still better than 12 amps
If he can run a 20 amp cable then he can connect it as a 240 volt 20A circuit, with a hardwired 16A L-2 EVSE. He just needs to connect (and label!) the unnecessary neutral wire as a second Hot wire.
Scarlet Ember 2018 Leaf SL W/ Pro Pilot
2009 Vectrix VX-1 W/18 Leaf modules, & 3 EZIP E-bicycles.
BAFX OBDII Dongle
PLEASE don't PM me with Leaf questions. Just post in the topic that seems most appropriate.

rmay635703
Posts: 540
Joined: Wed Jan 19, 2011 7:43 pm

Re: 120V to 240V Transformer

Fri May 17, 2019 5:23 am

LeftieBiker wrote:
rmay635703 wrote:Just a note most every leaf will charge at least 16amps even on 110vac with a proper EVSE AND outlet.

20amp 120vac circuits are quite common and even the classic 30/50 amp. 110vac RV plugs aren’t unheard of

If he doesn’t care about the 1900 watt charge rate it is possible he could get a 20 amp 110vac outlet and evse.

It’s still better than 12 amps
If he can run a 20 amp cable then he can connect it as a 240 volt 20A circuit, with a hardwired 16A L-2 EVSE. He just needs to connect (and label!) the unnecessary neutral wire as a second Hot wire.
True but why would he need to run cable?

Every house I’ve ever been in had a 20 amp or 30 amp breaker with 12 or 10 gage wires running to a string of outlets, if his breaker is already one of those ratings he can easily have one outlet swapped out for a 20 or 30 amp style matching his breaker rating

webeleafowners
Posts: 1018
Joined: Mon Oct 05, 2015 5:37 pm
Delivery Date: 06 Oct 2015
Location: Okanagan Valley British Columbia

Re: 120V to 240V Transformer

Fri May 17, 2019 6:25 am

cpthk wrote:Thanks, everyone.

Is there a thing to plug from two 120V outlet and adds up the wattage? Of course I would connect from two outlets from different rooms that do not share the same circuit breaker.
Yep. It’s called a “Quick 220”. Combines two 120 volt opposite leg circuits to make 240 volt. There is a 15 amp and a 20 amp model. Neither circuit can be a GFCI. It does it in a safe manner so if one side fails it kicks off both. Most people get the 15 amp model because that’s what the breakers are.

Then you need an LCS-15 clipper creek EVSE. You will have a 12 amp 240 volt EVSE that will charge your EV more than twice as fast as standard 120.

There is at least one and maybe two townhouses in our community doing this. Although we don’t use the Quick 220 device we do have an LCS-15 EVSE. Works well.

Having said all that, getting a 20 or even 50 amp line pulled might not be that much more than one of these devices...if at all.
2015 Smart Electric Drive convertible.
2016 Nissan Leaf SV 30KWh
EV only Family...well except for the big diesel motorhome. :shock:

Oilpan4
Gold Member
Posts: 1137
Joined: Wed Jan 09, 2019 10:51 pm
Delivery Date: 10 May 2018
Leaf Number: 004270

Re: 120V to 240V Transformer

Fri May 17, 2019 7:57 am

Just because the receptacles are in different rooms doesn't automatically mean they are on different breakers.

I do most of my charging with the original 12 amp Panasonic made granny evse that I converted to 240v.
2011 white SL leaf with 2014 batt.
Chargers: Panasonic brick moded for 240v, duosida 16a 240v and a 10kw setec portable CHAdeMO
Location: 88103

User avatar
davewill
Posts: 5083
Joined: Thu Mar 17, 2011 6:04 pm
Location: San Diego, CA, US

Re: 120V to 240V Transformer

Fri May 17, 2019 10:29 am

rmay635703 wrote: True but why would he need to run cable?

Every house I’ve ever been in had a 20 amp or 30 amp breaker with 12 or 10 gage wires running to a string of outlets, if his breaker is already one of those ratings he can easily have one outlet swapped out for a 20 or 30 amp style matching his breaker rating
They have? Most houses I've seen have 14 gauge wire with 15a breakers. They will often have a bigger circuit or two going to the kitchen, but that one is almost always loaded with kitchen appliances and not available for EV charging.
2014 Rav4 EV, Blizzard Pearl White
2011 LEAF SL w/QC, Blue Ocean, returned at end of lease

LeftieBiker
Moderator
Posts: 13993
Joined: Wed May 22, 2013 3:17 am
Delivery Date: 30 Apr 2018
Location: Upstate New York, US

Re: 120V to 240V Transformer

Fri May 17, 2019 12:31 pm

davewill wrote:
rmay635703 wrote: True but why would he need to run cable?

Every house I’ve ever been in had a 20 amp or 30 amp breaker with 12 or 10 gage wires running to a string of outlets, if his breaker is already one of those ratings he can easily have one outlet swapped out for a 20 or 30 amp style matching his breaker rating
They have? Most houses I've seen have 14 gauge wire with 15a breakers. They will often have a bigger circuit or two going to the kitchen, but that one is almost always loaded with kitchen appliances and not available for EV charging.
I agree. There is often at least one "appliance" circuit that is 20A, but you can't convert a multi-outlet circuit to 240 volts, and you can't use that awful "Quick 220" with just one leg. I was talking about options IF new cable had to be run, BTW, not saying that cable must be run.
Scarlet Ember 2018 Leaf SL W/ Pro Pilot
2009 Vectrix VX-1 W/18 Leaf modules, & 3 EZIP E-bicycles.
BAFX OBDII Dongle
PLEASE don't PM me with Leaf questions. Just post in the topic that seems most appropriate.

martyscholes
Posts: 47
Joined: Wed Dec 12, 2018 2:40 pm
Delivery Date: 12 Dec 2018
Leaf Number: 303385
Location: Colorado Springs

Re: 120V to 240V Transformer

Fri May 17, 2019 2:27 pm

Oilpan4 wrote:You will be far better off doing it right.
Cut sheet rock, drill holes, pull wire, be happy.
It's just part of EV ownership.

Unless you were already wired up for big welders, plasma cutter, large air compressors and therefore already had easy access to multiple big 240v plugs in your driveway/ garage area.
I agree, but I can relate to the OP comment. In my case, I bought a LEAF but have restrictions to rewiring the house. Every electrician said I need a service upgrade. The lowest estimate I received was $4,000 to upgrade the panel and run a 40-amp circuit. That is bad enough, but I am in the middle of a divorce where it is unclear whether or not I will keep the house, so there is no point in spending the money right now. Even if I wanted to spend the money, I cannot spend money outside of normal, everyday expenses while the divorce is underway. To make it even more interesting, I have no room in the garage, so I need a level-2 cable that will fit under the garage door.

My solution was to buy a 40 amp breaker, 35 feet of 8/3 uf wire, and a 14-50 receptacle from the local hardware store. I was able to connect the wire to the breaker inside the box and run it along the inside wall of the garage to a 14-50 receptacle attached to the included EVSE that is coiled up on a rolling stool. When I need to charge, I roll the stool out of the garage and the flat cable fits neatly under the closed garage door.

The whole project cost $130 and a Saturday afternoon.

rmay635703
Posts: 540
Joined: Wed Jan 19, 2011 7:43 pm

Re: 120V to 240V Transformer

Fri May 17, 2019 2:51 pm

davewill wrote:
rmay635703 wrote: True but why would he need to run cable?

Every house I’ve ever been in had a 20 amp or 30 amp breaker with 12 or 10 gage wires running to a string of outlets, if his breaker is already one of those ratings he can easily have one outlet swapped out for a 20 or 30 amp style matching his breaker rating
They have? Most houses I've seen have 14 gauge wire with 15a breakers. They will often have a bigger circuit or two going to the kitchen, but that one is almost always loaded with kitchen appliances and not available for EV charging.
This must be regional, I should photo my current box , not a single 15 amp breaker in my panel, I’m going down to see the panel in this home now

rmay635703
Posts: 540
Joined: Wed Jan 19, 2011 7:43 pm

Re: 120V to 240V Transformer

Fri May 17, 2019 2:57 pm

My relatives house has
9 20 amp breakers
3 15 amp breakers labeled “lighting”
1 double throw 40amp
1 double throw 30 amp
1 double throw 20 amp

Not a single 15 amp that goes to an outlet to be seen.

And I can’t attach a photo since this forum is stuck in 1994, this is the only forum I have belonged to that doesn’t allow attachments (excluding bravenet in 1998)

jjeff
Posts: 2047
Joined: Wed Jan 13, 2016 9:10 am
Delivery Date: 13 Jul 2014
Leaf Number: 422121
Location: MSP MN

Re: 120V to 240V Transformer

Fri May 17, 2019 4:12 pm

cpthk wrote:Thanks, everyone.

Is there a thing to plug from two 120V outlet and adds up the wattage? Of course I would connect from two outlets from different rooms that do not share the same circuit breaker.
I built my own but here's one already made and has features mine doesn't. Note as someone else said, the 2 120v outlets need to be on a different phase of your panel. A panel that has the ability for 240v(almost all except very old ones) will have both a A and B side, to use something like the Quick220v device you need to find a outlet on the A and then B side, otherwise it won't work, you'll just get 0v between the 2 outlets.
https://www.quick220.com/
2012 SL purchased used 2/'16
2013 S w/QC purchased new
Juicebox Premium 60a L1/L2 EVSE, Ebusbar 16a L1/L2 EVSE
'12 EVSEupgrade'd 20a L1/L2 EVSE, '13 EVSEupgrade'd adjustable 6-20a L2, 6-13a L1 EVSE
Zencar 13, 20, 30a L1/L2 portable EVSE
GE Durastation 30a