LTLFTcomposite
Well-known member
If you put a continuous 40a load on a 40a circuit with #8 wire will it overheat the wire and/or trip the breaker or is it just that there is no cushion if the breaker is a little weak?
LTLFTcomposite said:If you put a continuous 40a load on a 40a circuit with #8 wire will it overheat the wire and/or trip the breaker or is it just that there is no cushion if the breaker is a little weak?
It may trip the breaker, or it may not. The breaker is not required to hold, but it is not required to trip. Depends on the ambient temperature at the breaker, heating from other breakers, etc. The #8 wire will be fine, it is rated for 40a continuous.LTLFTcomposite said:If you put a continuous 40a load on a 40a circuit with #8 wire will it overheat the wire and/or trip the breaker or is it just that there is no cushion if the breaker is a little weak?
You are good as long as you don't charge for more than 3 hours. I do it all the time, haven't popped a breaker yet.LTLFTcomposite said:So if the Tesla draws 40a and you have a 40a circuit instead of the preferred 50a circuit the worst you are looking at is nuisance trips?
pchilds said:You are good as long as you don't charge for more than 3 hours. I do it all the time, haven't popped a breaker yet.LTLFTcomposite said:So if the Tesla draws 40a and you have a 40a circuit instead of the preferred 50a circuit the worst you are looking at is nuisance trips?
I'd say that the worst you are looking at is starting a fire, because the circuit has a marginal connection that works OK at 32A continuous but overheats at 40A continuous. If the circuit is installed properly, the worst you'd be looking at is nuisance trips. However, I wouldn't be comfortable doing it on an unknown circuit.LTLFTcomposite said:So if the Tesla draws 40a and you have a 40a circuit instead of the preferred 50a circuit the worst you are looking at is nuisance trips?
nsayer said:I've never heard of the continuous duty derating being based on the length of time the load is engaged. I would have assumed that any load with a very high duty cycle would require a derating. I believe I've been told or read that the NEC considers EV charging to be continuous duty regardless of how long you do it.
LTLFTcomposite said:Still wondering if that neutral can be put to any use though.
Maxstang said:Hello all! New Leaf owner here :mrgreen: and I've been enjoying my ride for 5 whole days! After much research (thanks to this forum), I've decided to upgrade the stock EVSE using EVSEUpgrade instead of purchasing a dedicated unit. I'll need to install the correct NEMA L6-30R receptacle in my garage but I'm wondering what you all think about what size breaker and what gauge wire to use. I realize I only need a 30A circuit for the EVSEupgrade, but installing a larger capacity best Modular Electrical Systemwould provide a more future proof installation should I decide to get a larger capacity EVSE in the future. There is also the question of 4 vs 3 conductor wire in case I need a neutral at some point. Thoughts?