Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 5:03 am

I used to live by the old rule of thumb that 6 was for 50, 8 for 40 and so on, but have come to learn that it's more complicated depending on the C rating. Is romex (or NM) always 60C? Seems like that should be 55A max, is a 60A breaker "close enough"?
LTL
White 2012 SV delivered 10 Dec 2011 returned 25 Nov 2014 replaced with stopgap ICE Sentra
[35 months] [35K miles] [9 Bars]
2013 Volt replaced after 36 months/30k miles with ICE Rogue
2016 SV-adjacent May 2016 lost 4th bar March 2018

wwhitney
Posts: 751
Joined: Sat Jul 17, 2010 10:10 am
Delivery Date: 01 Apr 2011
Location: Berkeley, CA

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 8:19 am

NM cable is limited to the base 60C ampacity (*). So #6 NM typically has an ampacity of 55A. Since 55A is not a standard breaker size, it is permissible to protect it with a 60A breaker, provided that the calculated load is 55A or less.

As an example, suppose you had an EVSE that can be set to a pilot signal of 44A. Then the required ampacity is 55A, and you could use 6/2 NM on a 60A breaker. But if the pilot signal is the more typical 48A, the required ampacity would be 60A, and you'd need to use either 4/2 NM or #6 conductors with a 75C wiring method (for a 65A ampacity).

Cheers, Wayne

(*) The actual conductors in NM cable are 90C conductors. For purposes of temperature or bundling "derating", that means you can start at the 90C ampacity when applying the correction factors. The allowable ampacity is then the lesser of the base 60C ampacity and the corrected 90C ampacity.

User avatar
LTLFTcomposite
Posts: 4661
Joined: Fri Apr 23, 2010 6:06 pm
Delivery Date: 10 Dec 2011
Leaf Number: 5926
Location: Central FL

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 8:53 am

Wayne, thanks very much for the reply and as always complete answer.
LTL
White 2012 SV delivered 10 Dec 2011 returned 25 Nov 2014 replaced with stopgap ICE Sentra
[35 months] [35K miles] [9 Bars]
2013 Volt replaced after 36 months/30k miles with ICE Rogue
2016 SV-adjacent May 2016 lost 4th bar March 2018

camasleaf
Posts: 640
Joined: Sun Sep 26, 2010 5:20 am
Delivery Date: 17 Jun 2011
Location: Camas, WA

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 12:42 pm

NM-B is rated at 90C base load. When I looked at Home Depot pretty much all they had in store was NM-B. Unless is an older cable it, might actually be NM-B.

Still need to use 75C column since most breakers terminals are only rated 75C.

Either way 60A breaker will work, but with NM-B 48A EVSE would be OK.
2011 SLe 06/17/11 Over 86000 miles 64%SOH 14.2kWh
2018 Honda Clarity PHEV
5.7kW DC System

wwhitney
Posts: 751
Joined: Sat Jul 17, 2010 10:10 am
Delivery Date: 01 Apr 2011
Location: Berkeley, CA

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 1:48 pm

On the contrary,

2011 NEC wrote:334.80 Ampacity. The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The allowable ampacity shall not exceed that of a 60°C (140°F) rated conductor. The 90°C (194°F) rating shall be permitted to be used for ampacity adjustment and correction calculations, provided the final derated ampacity does not exceed that of a 60°C (140°F) rated conductor.

Cheers, Wayne

camasleaf
Posts: 640
Joined: Sun Sep 26, 2010 5:20 am
Delivery Date: 17 Jun 2011
Location: Camas, WA

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 3:36 pm

I stand corrected. I was thinking about NMD90.
2011 SLe 06/17/11 Over 86000 miles 64%SOH 14.2kWh
2018 Honda Clarity PHEV
5.7kW DC System

User avatar
LTLFTcomposite
Posts: 4661
Joined: Fri Apr 23, 2010 6:06 pm
Delivery Date: 10 Dec 2011
Leaf Number: 5926
Location: Central FL

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 6:49 pm

wwhitney wrote:...provided that the calculated load is 55A or less.

One more question, this is feeding a small (four space) sub panel, is the "calculation" the sum of the amps of the breakers in the sub panel? As a practical matter none of these loads is continuous, eg a boat lift. Basically we have 6/3 romex feeding a string of LED Christmas lights on the dock :-D
LTL
White 2012 SV delivered 10 Dec 2011 returned 25 Nov 2014 replaced with stopgap ICE Sentra
[35 months] [35K miles] [9 Bars]
2013 Volt replaced after 36 months/30k miles with ICE Rogue
2016 SV-adjacent May 2016 lost 4th bar March 2018

wwhitney
Posts: 751
Joined: Sat Jul 17, 2010 10:10 am
Delivery Date: 01 Apr 2011
Location: Berkeley, CA

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 7:36 pm

LTLFTcomposite wrote:One more question, this is feeding a small (four space) sub panel, is the "calculation" the sum of the amps of the breakers in the sub panel?

No, the calculation is done per Article 220 of the NEC. As a practical matter, the sum of the breakers will be an overestimate of the load, often a very large overestimate. On the other hand, if the run is long, you will need to upsize the conductors to account for voltage drop.

LTLFTcomposite wrote:As a practical matter none of these loads is continuous, eg a boat lift. Basically we have 6/3 romex feeding a string of LED Christmas lights on the dock :-D

This 6/3 Romex is only for the indoor portion of the run? Because NM cable is only for use in dry locations, and any outdoor location (even inside conduit) is considered a wet location.

Cheers, Wayne
Last edited by wwhitney on Sat Dec 29, 2018 7:37 pm, edited 1 time in total.

wwhitney
Posts: 751
Joined: Sat Jul 17, 2010 10:10 am
Delivery Date: 01 Apr 2011
Location: Berkeley, CA

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 7:37 pm

camasleaf wrote:I stand corrected. I was thinking about NMD90.

That's a Canadian term, right? I think the Canadian Electrical Code is a bit more enlightened in this regard and doesn't restrict NM cable to the 60C ampacity, although I don't know the details.

Cheers, Wayne

User avatar
LTLFTcomposite
Posts: 4661
Joined: Fri Apr 23, 2010 6:06 pm
Delivery Date: 10 Dec 2011
Leaf Number: 5926
Location: Central FL

Re: Is a 60A breaker ever OK on 6/3 romex?

Sat Dec 29, 2018 8:02 pm

Yes, the 6/3 is just to feed the sub panel on the side of the house where two GFCIs feed individual wires in carlon to the dock area, a 20A single pole for outlet and lights and double pole for the lift. The circuit feeding the sub panel was oversized for possible addition of a pool. The 120v circuit is #12 and the lift is #10 per manufacturer specs (I suppose on account of voltage drop concerns, it's nearly 100' to the lift).
One thing I puzzled over was the ground wire, it seemed like it should have been sufficient to run a single ground wire for both circuits to the dock, maybe #8, but it was cheaper to do a 10 and a 12 so each has it's own ground.