The ampacity table is for 3 current carrier conductors in the conduit. I do not believe we are allowed to rate up for only 2 current carrier conductors. But it is good point, I will look to see if NEC allows any up rate.

For quick conduit fill I usualy use: https://www.southwire.com/calculator-conduit
 
https://ieeexplore.ieee.org/iel7/6287639/8600701/08669748.pdf

An interesting paper. A 50A breaker with 40A load will trip at 75C ambient. So my setup 100A breaker, #4 wire at 80A will work but only because #4 is rated 85A/75C and at 80A should not quite reach 75C and therefore not trip the breaker. All this discussion assumes 30C ambient temperature. In PNW the garage where the panel is will I rarely see 20C. In Arizona ....
 
That's a really good find on the paper that investigated the linear temperature sensitivity of trip current for 4 brands of breakers. i think the extrapolation to higher temperatures is reasonably valid and useful based on my experience.

For example a freestanding metal electrical box can easily reach 75C in direct sun. i have used 1/2" thick foam insulation sheets to line the inside of Hoffman boxes that were outdoors with full sun exposure.
 