AlanSqB said:
NEC 625.41 (formerly 625.14) defines an EVSE as a continuous load for the purposes of rating. The exception is if there is a hardware solution to manage the load in a way that does not exceed the rated capacity of the circuit. That solution does not include "I know I'm not going to plug it into a Tesla." It would include a "smart" EVSE that knows it's only allowed to pull so many amps for so long and adjusts itself accordingly.
All EVSE's have a set limit. One should set the limit (or buy one with a preset limit) of their EVSE to not exceed the the circuit onto which it is attached (NEC 625.41). My EVSE is set to 28A (30A is acceptable as well), the Leaf that I charge is set to 27.5A max from the factory, and the EVSE has a timer (as well as the Leaf). The Leaf will not accept 27.5 A for longer than 3 hours (I have tested this on a 6.6Kw SL).
This meets the "exception" of NEC 625.41 for a permenant installation (mine is not). This is a non-continuous load. And it didn't cost thousands for an electrician to come wire me a special EVSE circuit. It is not required.
I will tell everyone to get educated and make a proper assessment of their sutuation and not buy into the fear mongering that implies it is unsafe to have a EVSE charging at 27.5A on a 30A circuit just because it is an EVSE. Even if they own a Tesla.
Let me just add that the argument that the circuit needs to be inspected for degraded conditions, insulation, etc. applies to any type of load. Just because one uses 24A instead of 27.5A does not make it any safer.