When I use the included EVSE, the heavy black box is hanging and seems to be creating a lot of stress to the plug. This happens because my outlet is three feet from the ground. Is the EVSE built to be used this way?
No protection from what? I would like to understand that better. Seems no different than any other portable charger with a 5' cord.planet4ever said:NEC says the EVSE must be no more than about a foot from the outlet because there is no safety protection between the two of them.
Pirates and Ninjas. Apparently though it does protect against Zombies...smkettner said:No protection from what?
I was thinking more like this one:jcesare said:I bought one of these in Blue Ocean
http://www.lowes.com/pd_242113-66906-UTK500830_0__?productId=3190815&Ntt=utilitech++50%27+&pl=1¤tURL=%2Fpl__0__s%3FNtt%3Dutilitech%2B%2B50%2527%2B
I asked about the cord length at the Nissan Tour event and was told that the American engineers had complained about it but the Japanese engineers insisted on the short length. Maybe the outlets in Japan are 6 inches from the floor?sdbonez said:I had Nissan actually call for my feedback on the included EVSE a few weeks back. This was my primary concern and they echoed that they had received similar feedback from several others. (Have to believe they find a way for a slight redesign for the next model year)
smkettner said:I was thinking more like this one:jcesare said:I bought one of these in Blue Ocean
http://www.lowes.com/pd_242113-66906-UTK500830_0__?productId=3190815&Ntt=utilitech++50%27+&pl=1¤tURL=%2Fpl__0__s%3FNtt%3Dutilitech%2B%2B50%2527%2B
http://www.google.com/products/cata...X&ei=lrXKTbH9HYKTtwfDz7XmBw&ved=0CJwBEPMCMAg#
Ingineer said:I advise that you DO NOT use an extension cord unless you absolutely have to.
There are 2 holes in each end of the EVSE that can be used to put a hook or screw in for hanging. A bungee cord fits well, and can solve the problem. You could also screw a small hook into the stud near your outlet for this purpose.
If you must use a cord, make sure it's a minimum of #14AWG if it's kept down to a few feet. Anything longer (up to 50 feet) should be #12AWG. Over this should be #10AWG.
These recommendations apply on either 120v or 240v. Use cords with L6-20 ends for 240v. Do NOT under any circumstances make an adapter that allows you to put 240v into a "standard" extension cord!!!
This web site has the safe L6-20 #12AWG extension cords. I have 2 of the #7800 25 footers in my trunk along with a few adapters and that covers almost any 120/240v charging need.
-Phil
I just bought the 25 ft. version of that same cord, and I don't even have my Leaf yet! (The "week of" window has come and gone...)jcesare said:I bought one of these in Blue Ocean
http://www.lowes.com/pd_242113-66906-UTK500830_0__?productId=3190815&Ntt=utilitech++50%27+&pl=1¤tURL=%2Fpl__0__s%3FNtt%3Dutilitech%2B%2B50%2527%2B
No, the J1772-2010 standard specifically states that a level 1 EVSE is required to have a cord with a maximum length of 305 mm between the power outlet and EVSE.jcesare said:I asked about the cord length at the Nissan Tour event and was told that the American engineers had complained about it but the Japanese engineers insisted on the short length. Maybe the outlets in Japan are 6 inches from the floor?sdbonez said:I had Nissan actually call for my feedback on the included EVSE a few weeks back. This was my primary concern and they echoed that they had received similar feedback from several others. (Have to believe they find a way for a slight redesign for the next model year)
DarkStar said:No, the J1772-2010 standard specifically states that a level 1 EVSE is required to have a cord with a maximum length of 305 mm between the power outlet and EVSE.
Since J1772 compliance is based on those testing requirements, you can't really change the design without needing to retest again. Also, since 305 mm equals 12 inches it really is a draw either way...Ingineer said:DarkStar said:No, the J1772-2010 standard specifically states that a level 1 EVSE is required to have a cord with a maximum length of 305 mm between the power outlet and EVSE.
This is not true, you are misreading the standard. The 305mm requirement is for the test setup for radiated immunity testing.
The only mention of supply cable length I am aware of is in the NEC article 625.22, and it specifies:
"Regarding cord-and plug-connected EVSE, the interrupting device of a listed personnel protection system shall be provided and be an integral part of the attachment plug or be located in the power supply cable not more than 12 inches from the attachment plug."