A friend recently purchased a house, built in the early 00s, one thing I noticed was a nice 6-30 outlet in the garage along with a 6kw electric heater mounted to the ceiling with a corresponding 6-30 plug. I measured the outlet early on and noted it seemed to have power, 120v on each leg, 240v between the hots. It had a 30a breaker feeding the outlet and I thought it would be a nice way to charge my Leaf at up to 24a should I take it there. I've been taking the Prius because it's around 60+ miles one way and on a crazy freeway where if you're not doing 75mph you'll get blown off the road, it's only two lanes each way and almost always bumper to bumper in both lanes. IMO the particular stretch of I94 is the busiest and fastest stretch of freeway in our state, a major artery for people going E/W, both for in-state travel and people just passing through. Because of this, I figured I'd need all of my 11 bar 24kw Leaf battery, I wouldn't even attempt it with my 8 bar Leaf. Once to his house, I'd need to be plugged in the whole time I was there and the fastest charge rate the better, at 24a it would take around 5h for a full charge.
Anyway, I was there yesterday again with my Prius and this time he asked if I could look at his heater and why it wasn't working. I popped off the bottom of the heater and noted I was only getting one hot. I unplugged the heater and like before measured 120v to each hot, 240 between them. I figured it had to be either something in the plug or the 4' of flexible conduit between the two. I first took apart the plug and immediately saw the problem, the wire going to one of the prongs was burnt completely through, a chard mess, I could also see the prong had a bluish tint, probably from getting so hot. I couldn't figure how or why it had gotten so hot but when I looked inside the slot in the outlet I could see one of the hot sides had more space(not as tight) as the other side. I shut the 30a breaker off, measured for any voltage to the outlet and when I verified there was none I took the melted prong out of the plug and holding on to the back end with a needle nose pliers I manually inserted the plug into each side and found one side slid in and out much easier than the other, probably resulting in some resistance which after a long time could have easily caused heat build-up, possibly resulting in the melted plug.
Next, I removed the cover plate to the outlet and to me the wiring didn't look like the minimum 10g wire I would have expected but lucky to be 12g. Whoever ran this outlet, and I totally believe it was done after initial construction, probably by the homeowner or a clueless friend, had used Romex wiring inside a narrow plastic conduit(1/2"?) I don't know how they managed to pull it through but they did. Initially, I couldn't see enough of the Romex jacket to see the gauge listed on the jacket but I was sure it wasn't 10g. Well as long as I had this much time invested and was planning on replacing the outlet and plug I pulled the outlet out and then I could see the 12g on the side of the jacket :shock: So whoever ran the wiring used 12g inside a tight conduit, used a 30a breaker and a 30a plug, all hooked to a 25a heater than probably ran 24x7 or damn near!
I can't believe that the wiring never melted or burned down the house but for the most part, the Romex looked fine, it was just the plug that failed, melted into a globby mess. Needless to say, I'm going to rework the outlet for my friend, take out the 30a breaker, inspect the wiring going to it, and hopefully, it will look OK. Next will be to get rid of the junky 6-30 outlet and plug and instead install a quality L6-20 twist-lock plug outlet to his heater and lastly rewire the heater to only draw 13.7a which according to the schematic on the bottom of the heater is possible by adding/removing some jumpers. Currently, the heater looks to be configured for the max 6kw, which again I can't believe didn't cause their 12g wiring to fail.
Long story short, I'm sure glad I didn't plug my Leaf into that outlet and charge much, kinda a bummer I'll be restricted to 16a in the future as he will for his ceiling heater but the outlet is quite a ways from his basement breaker box and has several areas with sheetrock ceilings so running new 10g or if I were to go through that much trouble I'd probably want to run 8 or even 6g so I could put a 14-50 RV plug for him. Boy I can't believe how someone would have done that, as I told my friend, whoever wired that outlet "knew enough to be dangerous" :shock:
Anyway, I was there yesterday again with my Prius and this time he asked if I could look at his heater and why it wasn't working. I popped off the bottom of the heater and noted I was only getting one hot. I unplugged the heater and like before measured 120v to each hot, 240 between them. I figured it had to be either something in the plug or the 4' of flexible conduit between the two. I first took apart the plug and immediately saw the problem, the wire going to one of the prongs was burnt completely through, a chard mess, I could also see the prong had a bluish tint, probably from getting so hot. I couldn't figure how or why it had gotten so hot but when I looked inside the slot in the outlet I could see one of the hot sides had more space(not as tight) as the other side. I shut the 30a breaker off, measured for any voltage to the outlet and when I verified there was none I took the melted prong out of the plug and holding on to the back end with a needle nose pliers I manually inserted the plug into each side and found one side slid in and out much easier than the other, probably resulting in some resistance which after a long time could have easily caused heat build-up, possibly resulting in the melted plug.
Next, I removed the cover plate to the outlet and to me the wiring didn't look like the minimum 10g wire I would have expected but lucky to be 12g. Whoever ran this outlet, and I totally believe it was done after initial construction, probably by the homeowner or a clueless friend, had used Romex wiring inside a narrow plastic conduit(1/2"?) I don't know how they managed to pull it through but they did. Initially, I couldn't see enough of the Romex jacket to see the gauge listed on the jacket but I was sure it wasn't 10g. Well as long as I had this much time invested and was planning on replacing the outlet and plug I pulled the outlet out and then I could see the 12g on the side of the jacket :shock: So whoever ran the wiring used 12g inside a tight conduit, used a 30a breaker and a 30a plug, all hooked to a 25a heater than probably ran 24x7 or damn near!
I can't believe that the wiring never melted or burned down the house but for the most part, the Romex looked fine, it was just the plug that failed, melted into a globby mess. Needless to say, I'm going to rework the outlet for my friend, take out the 30a breaker, inspect the wiring going to it, and hopefully, it will look OK. Next will be to get rid of the junky 6-30 outlet and plug and instead install a quality L6-20 twist-lock plug outlet to his heater and lastly rewire the heater to only draw 13.7a which according to the schematic on the bottom of the heater is possible by adding/removing some jumpers. Currently, the heater looks to be configured for the max 6kw, which again I can't believe didn't cause their 12g wiring to fail.
Long story short, I'm sure glad I didn't plug my Leaf into that outlet and charge much, kinda a bummer I'll be restricted to 16a in the future as he will for his ceiling heater but the outlet is quite a ways from his basement breaker box and has several areas with sheetrock ceilings so running new 10g or if I were to go through that much trouble I'd probably want to run 8 or even 6g so I could put a 14-50 RV plug for him. Boy I can't believe how someone would have done that, as I told my friend, whoever wired that outlet "knew enough to be dangerous" :shock: