RustyShackleford
Well-known member
At our vacation house, I installed a ductless minisplit heal-pump (to partially replace existing electric-resistance heat). Thinking I might want to add 1 or 2 additional minisplits in the future, I put in a 40 amp subpanel (fed with 8/3 NM-B and protected by a 40 amp breaker in the main panel). I've since had second thoughts about the additional minisplits - even with some rental, the house is nowhere close to continuously-occupied, especially in the winter - and this changes the economics.
Meanwhile, I'm interested in providing Level2 EV charging capability there. In another thread it was discussed that I cannot plug the Leaf factory EVSE into a 30amp dryer outlet, that I need a lower-amperage EVSE if I'm not going to install a dedicated circuit. So I'm thinking about installing a lower-amperage hard-wired EVSE, connected to this subpanel. I'm wondering what size is appropriate.
Currently the 40amp subpanel has the minisplit, protected by the recommended 20amp breaker, plus a 20amp 120vac "convenience" outlet. I know that the sum of breakers in a panel is allowed to exceed the breaker feeding that panel. So I believe it's ok for the EVSE to be larger than 20 amps (40amp subpanel minus 20amp minisplit). I'm thinking a 24amp EVSE is appropriate. I'd protect it with a 30amp breaker in the subpanel, and wire it using 10awg THWN (though I think maybe 12awg would suffice, if it's THWN-2) in PVC conduit.
Add'l info about the minisplit load: "minimum circuit ampacity is 16.5amps, and "maximum operating curren"t is 13.4 amps.
Does this sound right ? How do I compute what size EVSE it's reasonable/safe/code-compliant to add to my subpanel ?
Extra-credit problem: Assuming a 24amp EVSE is acceptable, Clipper Creek lists two diferent hard-wared 24amp units, the LCS-30 and the HCS-30; what is the difference between these two, other than price ?
Meanwhile, I'm interested in providing Level2 EV charging capability there. In another thread it was discussed that I cannot plug the Leaf factory EVSE into a 30amp dryer outlet, that I need a lower-amperage EVSE if I'm not going to install a dedicated circuit. So I'm thinking about installing a lower-amperage hard-wired EVSE, connected to this subpanel. I'm wondering what size is appropriate.
Currently the 40amp subpanel has the minisplit, protected by the recommended 20amp breaker, plus a 20amp 120vac "convenience" outlet. I know that the sum of breakers in a panel is allowed to exceed the breaker feeding that panel. So I believe it's ok for the EVSE to be larger than 20 amps (40amp subpanel minus 20amp minisplit). I'm thinking a 24amp EVSE is appropriate. I'd protect it with a 30amp breaker in the subpanel, and wire it using 10awg THWN (though I think maybe 12awg would suffice, if it's THWN-2) in PVC conduit.
Add'l info about the minisplit load: "minimum circuit ampacity is 16.5amps, and "maximum operating curren"t is 13.4 amps.
Does this sound right ? How do I compute what size EVSE it's reasonable/safe/code-compliant to add to my subpanel ?
Extra-credit problem: Assuming a 24amp EVSE is acceptable, Clipper Creek lists two diferent hard-wared 24amp units, the LCS-30 and the HCS-30; what is the difference between these two, other than price ?