Certainly, it is possible, but the simplest way to do it would not be compliant with the National Electrical Code. That is because a L6-20R must be protected at 20 amps or less, while your dryer plug should be on a 30 amp breaker.marccbr said:I have a used 3 prong 30 amp dryer connection on the otherside of my garage wall is it possible to share that circuit with a L6-20R? Would like to install a Levitron 160 and since its a rental, I hate to run a line from the box all the way across the house. Of course I would make sure not to run both the EVSE and the Dry at the same time. Also if it is possible would it be legal in most places?
So your NEC-compliant options are (1) to put in a L6-30R and use a L6-30P to L6-20R pigtail for your EVSE (2) put in a small subpanel or breaker enclosure for a 20 amp breaker for the L6-20R or (3) use a cover mounted switch/15 amp fuse combo with a L6-20R, but then you are limited to 12 amps for the EVSE.