MikeD said:bryan38401: You wrote (correctly, I think): "the hard wire is a nec code it depends on what year book you are using.". More specifically I believe it is related to Article 625.13 (Electric Vehicle Supply Equipment) reading in part "Electric vehicle supply equipment rated at 125 volts ... [additional requirements] ... shall be permitted to be cord-and-plug-connected. All other electric vehicle supply equipment shall be permanently connected and fastened in place." (2008 and 2011 versions).
However, a TIA (Tentative Interim Amendment (TIA 11-2) was issued in Oct 2011 that would permit non-portable electric vehicle supply equipment (under certain conditions like no more than 50a) rated up to 250 volts to be cord-and-plug connected. I believe it is this that allows non-direct wired 240v EVSEs (under the required conditions).
"A Tentative Interim Amendment is tentative because it has not been processed through the entire standards-making procedures. It is interim because it is effective only between editions of the standard. A TIA automatically becomes a proposal of the proponent for the next edition of the standard; as such, it then is subject to all of the procedures of the standards-making process."
I'd like to point out that regardless of the what NEC says about this issue Ecotality was having their Blink units installed with cord and plugs both inside and outside and these were obviously passing inspections.