mrbigh said:
TonyWilliams said:
Any ideas on a connector for 75 amps?
For a full 75 amp connection, I suspect this unnamed connector will connect to the pigtail that will go straight too the breaker box.
How about this Rosco 100 amp wire connector?
http://www.rosco.com/lighting/connectors.cfm" onclick="window.open(this.href);return false;
For removable connections and above the 50AMPs requirements, you better go the Anderson's line of connectors. The most appropriate would be the 175Amps.
So, I'm locked into 4 AWG conductor with these connectors, but only two conductors? That won't work.
http://www.bdbatteries.com/anderson175.php" onclick="window.open(this.href);return false;
UL Current Rating (Amperes)* 1 75 to 175*
UL Voltage Ratings (Volts) 600*
Contact Barrel Wire Size (AWG) 1/0 AWG to 4 AWG
(mm) 53.5 to 152
Maximum Wire Insulation Diameter (inches) 0.75 to 1.10
(mm) 19.1 to 27.9
AVG Contact Resistance* (micro-ohms) 100 to 50
Insulation Withstanding 2200
Test Voltage (Volts AC/DC)
Contact Retention Force (lbf) 300 to 500
Life
a. No load (Contact/Disconnect Cycles) To 10,000
b. Under Load (Hot Plug 250 cycles @ 120V) 75A to 100A*
Avg. Connection/Disconnect (lbf) 25 to 30
Operating Temperature Range °C** -20° to 105°
Flammability Rating of Housing Material UL94 V-0