No, a NEMA 10-30 Has a neutral but no dedicated ground. While it is true that neutral and ground are eventually connected at the bonding point, there is a difference. The center of the "crows foot" on a 10-30 may carry 120 volt loads between it and one of the "hot" wires. No current is permitted to be carried on a "ground".
If you look on a NEMA 10-30 device, it will be labeled 120-240 volt. This applies to all "10" series outlets.
A NEMA 6-30 is almost the same, except it only has two hots and ground and should only be connected to 240 volt loads. The difference between the two types (10-30 and 6-30) is what the "third wire" is there for.
Two pole GFI's breakers 50 amps and below have a neutral connection and can be used on circuits with both 240 and 120 volt loads on the breaker. 60 amp and above generally are 240 volt only GFI.
The NEMA 10 series are obsolete and only still exist to service existing installs. New "driers" and wiring for them should be 14-30 or if no 120 volt loads 6-30 can be used.
https://www.americord.com/nema-char...VINH-Apro0ngbuvr1uFytV7vSi_hbP5TLiqjAMMcVBoug
And another quote explaining the history:
21
NEMA 10 connectors are
ungrounded, 125/250V connectors which have been outlawed since 1966 when grounding came in.
Because of appliance industry lobbying, exception was made until 1996 for ranges and dryers
only. So we are dealing with really ancient codes here. The exception required that electrical wiring be 4-wire
as soon as old stocks of ungrounded cable were used up*, but that the legacy NEMA 10 connectors could be used
for ranges and dryers only.
The idea was that by about 1970, legacy stocks of 3-wire cable would be gone, and all cabling would provide 4 wires, and a person with a NEMA 10 connector could simply remove the connector and find a 4-wire connection fit for a NEMA 14.