Why does the 30A GE Wattstation require a 40A breaker?

My Nissan Leaf Forum

Help Support My Nissan Leaf Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Publius

Well-known member
Joined
Dec 27, 2012
Messages
141
Location
Rochester, NY
I'm not an electrician, so maybe I'm just showing my ignorance, but why does the 30A GE Wattstation suggest that we used a 40A breaker? :?:
 
The GE Wattstation is considered to be a "continuous load". Therefore, the breaker must be 125% the rating of the device. 30x1.25 = 37.5, so 40A is the next appropriate breaker size.
 
Weatherman said:
The GE Wattstation is considered to be a "continuous load". Therefore, the breaker must be 125% the rating of the device. 30x1.25 = 37.5, so 40A is the next appropriate breaker size.

Thanks!
 