The following two NEC articles relate to the "125% continuous load rule(s)":
2011 NEC Article 210.20(A) (Overcurrent Protection -- Continuous and Noncontinuous Loads): "Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load."
2011 NEC Article 625.14 (Rating) "Electric vehicle supply equipment shall have sufficient rating to supply the load served. For purposes of this article, electric vehicle charging loads shall be considered to be continuous loads."
The following two NEC articles relate to the "80% max receptacle load rule" (which apparently attempt to minimize the risk of overloading due to one big load on a multi-receptacle branch circuit), but is still probably good to know and respect:
2011 NEC Article 210.23(A)(1) (Permissible Loads -- 15- and 20-Ampere Branch Circuits -- Cord-and-Plug-Connected Equipment Not Fastened in Place): "The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating."
Article 210.21(B)(2) (Outlet Devices -- Receptacles -- Total Cord-and-Plug-Connected Load)
which is similar in purpose to the one just above and limits total load for a given receptacle to 80% of the branch circuit rating.
I am essentially asking why does the NEC have the above 125% rule for "Continuous Loads" (which appears to apply to EVSEs even for charging sessions less than 3 hours because of Article 625.14 above)? Any licensed electricians (or any others) who work with residential wiring for a living have some knowledge/insight they would like to share? I'm trying to elicit some understanding of this issue for the benefit of us all, not just be authoritative and quote NEC articles w/o the substance behind them -- and I apologize if my previous post offended people in its approach to raising the issue.
2011 NEC Article 210.20(A) (Overcurrent Protection -- Continuous and Noncontinuous Loads): "Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load."
2011 NEC Article 625.14 (Rating) "Electric vehicle supply equipment shall have sufficient rating to supply the load served. For purposes of this article, electric vehicle charging loads shall be considered to be continuous loads."
The following two NEC articles relate to the "80% max receptacle load rule" (which apparently attempt to minimize the risk of overloading due to one big load on a multi-receptacle branch circuit), but is still probably good to know and respect:
2011 NEC Article 210.23(A)(1) (Permissible Loads -- 15- and 20-Ampere Branch Circuits -- Cord-and-Plug-Connected Equipment Not Fastened in Place): "The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating."
Article 210.21(B)(2) (Outlet Devices -- Receptacles -- Total Cord-and-Plug-Connected Load)
which is similar in purpose to the one just above and limits total load for a given receptacle to 80% of the branch circuit rating.
I am essentially asking why does the NEC have the above 125% rule for "Continuous Loads" (which appears to apply to EVSEs even for charging sessions less than 3 hours because of Article 625.14 above)? Any licensed electricians (or any others) who work with residential wiring for a living have some knowledge/insight they would like to share? I'm trying to elicit some understanding of this issue for the benefit of us all, not just be authoritative and quote NEC articles w/o the substance behind them -- and I apologize if my previous post offended people in its approach to raising the issue.