wwhitney said:A slight elaboration on the 40A/50A model: 50A ampacity wiring is required, which for NM (Romex) cable or other wiring method limited to 60C ampacity is indeed #6 wire. However, if you end up using a 75C wiring method, such as THHN in EMT, you can use #8 conductors if both the breaker and the L6-50 outlet are rated for 75C terminations. I would expect them to be so rated, but it would need to be checked.greenleaf said:Actually, I plan on doing this myself. Here's the needed breaker(s) and wires
20A model (L6-20 outlet), 16A max output, breaker 20A, #12 wire
30A model (L6-30 outlet), 24A max output, breaker 30A, #10 wire
40A/50A model (L6-50 outlet), 40A max output, breaker 50A, #6 wire
The breaker needs to be dual-pole.
Cheers, Wayne
That is my spec in a 1" EMT, could easily pull 6 if needed. I like the idea of 9 kw capability.