SageBrush wrote:.....
208 volts it is on a WYE when measured between two 120 volt legs. All I needed was to add vectors correctly :oops:

Thanks to Gerry for the kind redirection.
Which is why basically all commercial power(larger places that use 3-phase) only have 208v instead of what we have at home, 120v/240v. To get a true 240v at a commercial building that uses 3 phase they need to have a special 240v transformer, which would only be used in cases where they truly needed 240v and not an equivalent 208v.
Lighting and high current draw devices on a 3-phase building could be 277v per leg or 480v between any 2 of the 3 legs of the transformer. Buildings that I've seen that use 480v have a 480v transformer outside the building and 3-phase 480v to 120/208v transformer/s inside the building to supply wall outlets and things that require 120v or 208v. Rooms that have the 480v to 208v transformers often get quite warm and require an exhaust fan or even cooling. Such rooms are a nice place to warm up in the winter after shoveling outside in sub-zero temps ;)
2012 SL purchased used 2/'16
2013 S w/QC purchased new
Juicebox Premium 60a L1/L2 EVSE, Ebusbar 16a L1/L2 EVSE
'12 EVSEupgrade'd 20a L1/L2 EVSE, '13 EVSEupgrade'd adjustable 6-20a L2, 6-13a L1 EVSE
Zencar 13, 20, 30a L1/L2 portable EVSE
GE Durastation 30a

RustyShackleford
Posts: 99
Joined: Mon Jun 24, 2019 4:59 pm
Delivery Date: 0- 0-2018
Location: central NC

Re: dumb question about quick charging

Thu Jul 04, 2019 4:09 pm

Wow, this thread has gone places !
2018 Nissan Leaf SV
2006 Subaru Outback 2.5i Ltd

Return to “EVSE / Charging Equipment and Networks”